I'm looking at a cable spec sheet for 1/C 2kV extra flexible power cable that will be used in a temporary installation. The ampacity table gives the ampacity for the different cable sizes based on 40deg C ambient temperature or 90deg C conductor temperature.
Even though these cables are rated at 90deg C can you use this rating if they will be connected to lugs/equipment rated for 75 deg C? If not than how do you go about getting the 75deg value for the same cable if not published by manufacturer?