electricalperson Senior Member Location massachusetts Jun 7, 2008 #1 to determine the conductor size for a romex cable you can use the 90 degree rating in 310.16 but the final ampacity cant be over the ampacity in the 60 degree rating?
to determine the conductor size for a romex cable you can use the 90 degree rating in 310.16 but the final ampacity cant be over the ampacity in the 60 degree rating?
chris kennedy Senior Member Location Miami Fla. Occupation 60 yr old tool twisting electrician Jun 7, 2008 #2 electricalperson said: to determine the conductor size for a romex cable you can use the 90 degree rating in 310.16 Click to expand... Yes 110.14(C) but the final ampacity cant be over the ampacity in the 60 degree rating? Click to expand... Yes 240.4(D)
electricalperson said: to determine the conductor size for a romex cable you can use the 90 degree rating in 310.16 Click to expand... Yes 110.14(C) but the final ampacity cant be over the ampacity in the 60 degree rating? Click to expand... Yes 240.4(D)