Thanks again for guiding this mere mortal towards a better understanding of the ampacity tables. The Neher-McGrath equation hits the nail on the head Jon.
Here is some info on the development of table 310-16:
Quote from article:
"There are ampacity tables in the National Electrical Code that are sufficient for most installations. However, the tables in the NEC are very crude approximations and therefore include a substantial safety margin."
Never McGrath isn’t hard, just tedious. Lots of variables and calculations. The formula in the NEC is the tip of the iceberg. If you read the Neher-McGrath papers those exact same tables are in the five paper collection. When you use the NEC tables you are using the Neher-McGrath method. The papers are free from Neher-McGrath. So if there is any confusion just download and read them.
It’s 60, 75, or 90 C temperature RISE above an average ambient given in the heading of each table, 30 C. The maximum absolute wire temperature allowed is 120 C (90+30). If the average air temperature is 60 C to begin with you still use the table with the 90 C column in a 30 C temperature, then multiplier THAT by the deratjng factor for 60 C ambient. Do not use the 60 C RISE number in a 60 C space.
You run the calculation twice. Inside the raceway use the maximum rating for the wire. Derate for number of current carrying conductors. Most raceways use the chart a few tables back but tray for instance has its own derating rules. At the terminals run the calculation again but here you are limited by the rise of the terminal if it is lower than the wire which it usually is. However since it’s an open space like a gutter we don’t apply derating for number of conductors.
Now take the lower ampacity number.
We don’t normally actually do it twice in practice and the results will surprise you. For instance using #14 THHN with 75 C terminals we get 20 A in the conduit and 15 A at the terminals with 1-3 conductors. At 4-6 conductors we get 15 A after derating to 80% at 90 C. So contrary to popular belief by the engineering crowd you get 6 conductors “for free” at 90 C (modern, -2 insulation).
You can run the calculations yourself by hand. I’ve done it based on the tantalizing phrase that the tables are “very conservative” and that I’d get higher ampacities by doing the calculation. Lies, lies, lies. I get the same results as in the tables most of the time. Exceptions are buried cable if you deviate from the duct bank and cover specifications.