I have been contacted by a facilities manager for a large chiller plant that supplies cold water for a portion of a town. The problem with this is a pronounced ampacity imbalance. How is it occuring? Here are the particulars:A phase 814A, B phase 832A. C phase 731A. ACV 484, ABV 490, BCV 489. The service grounds are excellent reading less than one ohm. There are two chillers in the building. Only one was running while I was there, but I was assured that the second one had the same issue. Two power company pad mount transformers feed two sets of switchgear in the building. Both sets of gear were scanned with FLIR cameras with no hot spots. All connections appear clean, bright and tight. The power company switched their primaries, A to B, B to C, C to A, to see if the problem would follow. It did. The low ampacity originally was on B phase and now is on C phase. The power company says it is only responsible to keep voltage in a 1 percent range, and they are very close. I have not researched all possibilities yet, but was reaching out for ideas. Any body got some? Thanks, George