article 330 says that MC ampacity is going to be determined by 310.15. so 310.15 (B)(3) says that multicolor cables (Mc would be multicolor right?) installed without maintaining spacing for a continuous length longer than 24in. ( so a bundle of mc 12/3-12/2 as homeruns.) the allowable ampacity shall be reduced.
is there a exception about mc that allows me to run them in bundles without having to adjust the ampacity or do I just have to make sure they are separated. because if so then I wouldn't even be able to run two 12/2 together much less two or three or more 12/3 with out breaking this rule.
just want to make sure im interpreting this right and that im not missing something. i'm sure a lot of you have run bundles of mc in different projects.. .let me know what you guys end up doing.
thank you so much.
is there a exception about mc that allows me to run them in bundles without having to adjust the ampacity or do I just have to make sure they are separated. because if so then I wouldn't even be able to run two 12/2 together much less two or three or more 12/3 with out breaking this rule.
just want to make sure im interpreting this right and that im not missing something. i'm sure a lot of you have run bundles of mc in different projects.. .let me know what you guys end up doing.
thank you so much.