Per 334.80 we must use the 60 C column so the ampacity is 25 amps.

And we can use it at 25 amps for motors, HVAC equipment and many other applications.

240.4(D) limits the use of 12 AWG to 20 amps for some installations like branch circuits but that does not change the rating of the cable just how we use it.
 

ibew441dc

Senior Member
NM-B is Nonmetallic Sheathed cable type B ............ in other words regular old Romex. :smile:


That would be that old cloth stuff??? I don't recall ever seeing NM-B in the NEC.

I thought maybe that is what the OP was trying to point out:smile:
 

480sparky

Senior Member
Location
Iowegia
Type NM-B:

SouthwireLarge.gif


Wierd stuff, I tells ya! They can't even decide what color to make it. Some's white.... some's yeller, some's that icky orange. And when it's real thick, it's black as coal!
 

ibew441dc

Senior Member
334.112 Insulation. The insulated power conductors shall
be one of the types listed in Table 310.13(A) that are suitable
for branch-circuit wiring or one that is identified for
use in these cables. Conductor insulation shall be rated at
90?C (194?F).
FPN: Types NM, NMC, and NMS cable identified by the
markings NM-B, NMC-B, and NMS-B meet this
requirement.


Well would ya looky there......duuuhhhh:roll:
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
Question: What is the ampacity of a 12/2 NMB Cable?
How do you answer this when taking a Master Electrician's Exam?

I agree it is a poorly worded question. I my post #2, I quoted 334.80 because I thought the question read "How do you answer this when talking to a master electrician?" I retracted that because as Bob pointed out, there is more than one answer.
 

iwire

Moderator
Staff member
Location
Massachusetts
I think it is 20......and remember iwire....No Questioning!:grin:

So many questions.:D

What does T310.16 tell us?

What circuits does 240.4(D) apply to and did the question specify what type of circuit?

Where do you see anything about a 'rating' in 240.4(D)?

Article 240 does not have to do with conductor ratings it has to do with over current protection and 240.4(D) tells us what size OCPD we must use with 12 AWG in some applications. Article 240 can not change a conductors rating, only how we protect it.
 

ibew441dc

Senior Member
So many questions.:D

What does T310.16 tell us?

What circuits does 240.4(D) apply to and did the question specify what type of circuit?

Where do you see anything about a 'rating' in 240.4(D)?

Article 240 does not have to do with conductor ratings it has to do with over current protection and 240.4(D) tells us what size OCPD we must use with 12 AWG in some applications. Article 240 can not change a conductors rating, only how we protect it.

I'm catch'n what your throw'in as far as the directive stated in 334.80 but take a look at this http://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet6

although it may be unintended...it says 20 amps is the ampacity of 12/2.

Using the Southwire Brand Romex type NM-B, I think 110.3(B) comes into play.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician

480sparky

Senior Member
Location
Iowegia
I'm with Bob on this one. Ampacity is based on 310.16, where it says it's 25. 240.4(D) is about overcurrent protection, not ampacity.

It's the same thing when it comes to the top speed of a car, as opposed to the speed limit.
 

ibew441dc

Senior Member
This is a test question, and as the question reads, I agree with Bob.

Don't get me wrong, I agree with Bob too. I mean come on I was questioning the existence to NM-B at the beginning of this thread, and came to the conclusion that I knew what it was, but did not call it appropriately. Anytime I look something up for Romex, I'm think'n NM not NM-B....

For the sake of conversation though....based on the Southwire info what do you think the ampacity is for 12/2 NM-B?:smile:
 