mivey
Probably, but let's skip the nickle and dime stuff and use all your money, if the casinos could cover it.:wink:I am willing to bet all of your money the table will be revised. Bet, bet...huh?![]()
I remember speaking with John Canjemi of UL, and he has stated in the meetings that the manufacturer uses the standards as guidelines, but can write stricter labeling as long as it does not change the minimum of the Standard(s) they are required to adhere to.
"310.15....20"?? Don't see 20 amps until 240.4(D)(5). It is either a typo or outdated tables. I'm guessing outdated tables.
No need to guess. I've just sent an email to ask.
Type NM-B:
Wierd stuff, I tells ya! They can't even decide what color to make it. Some's white.... some's yeller, some's that icky orange. And when it's real thick, it's black as coal!
We have talked about this before and I still do not agree.
In order to list a product to a particular standard there are obligations you must meet, you can't say I choose not to meet all these obligations but still desire the same listing as another manufacturer that meets all the obligations.
Yep and we can't use that white here in NM (New Mexico) not Non Metallic. No 14 AWG allowed in construction here any more.
To see the inspector take a voltage reading at the meter then the breaker and then an outlet and you better not have a voltage drop of 5% between meter and breaker and 3 % between breaker and final device or you fail. So by getting rid of 14AWG they killed off the major reason for excessive voltage drops.
An inspector taking readings???
I wonder what kind of insurance they carry, it must be very, very expensive not to mention that would also change the workers comp they pay.
I also wonder what kind of PPE they use.
It does not sound like a very smart thing for them to be doing, paranoi is what comes to my mind when I read stuff like this.
Here that is not an FPN, the New Mexico Electrical Code makes 5% on the Service and 3 % on the runs a requirement.
http://www.nmcpr.state.nm.us/nmac/parts/title14/14.010.0004.htm.