Good morning, since I'm new to the forum this might have already been a topic. When sizing conductors for a 200 amp service, and a 100 amp service, why is it "common" to use 4/0 Aluminum for 200 amps and #2 for 100 amps in the 90° column when it states clearly on every termination point in the panel box we should size wire in the 75°column? 4/0 Aluminum is rated for 180 amps in the 75° column and #2 is rated for 90 amps in the 75° column. Is this because the calculated load will never exceed the amperage? What if its for agriculture purposes as well (non dwelling)? Can someone please simplify this. Thank you much