I have a 45 KW generator. I am trying to figure out how many amps each individual winding can handle safely without the thing lighting on fire.
Each winding makes 120 volts. 1t is a 12 lead machine which means that there are 6 windings.
The way I see it is 45,000 watts divided by 120 volts times .8 power factor = 300 amps (output of all windings at once)
Divide this by 6 windings = 50 amps per winding.
I have no clue why the name plate says 245 amps. Nor does it seem to specify at what voltage the 245 amps is at.
It's also curious why it says it's 1 phase while it's a 12 lead generator, and the voltage listed is 120/208. If anybody has any insight on this I would love to hear from you.
I have this machine wired in a double delta configuration for single phase; 120/240 volts (see schematic above)
That gives me (two) 3 phase 120 volt deltas connected together at a corner which makes the neutral. The way I see it; each delta can safely produce 100 amps@ 120 volts.
So I think I can safely pull 100 amps@ 240 volts or a total of 200 amps@ 120 volts (single phase).
To put it plainly, If the two single phase "hots" from the generator go through a 100 amp 240 volt breaker before the transfer switch, I should be good.
Does this sound reasonable to anybody here?
Thanks.
Each winding makes 120 volts. 1t is a 12 lead machine which means that there are 6 windings.
The way I see it is 45,000 watts divided by 120 volts times .8 power factor = 300 amps (output of all windings at once)
Divide this by 6 windings = 50 amps per winding.
I have no clue why the name plate says 245 amps. Nor does it seem to specify at what voltage the 245 amps is at.
It's also curious why it says it's 1 phase while it's a 12 lead generator, and the voltage listed is 120/208. If anybody has any insight on this I would love to hear from you.
I have this machine wired in a double delta configuration for single phase; 120/240 volts (see schematic above)
That gives me (two) 3 phase 120 volt deltas connected together at a corner which makes the neutral. The way I see it; each delta can safely produce 100 amps@ 120 volts.
So I think I can safely pull 100 amps@ 240 volts or a total of 200 amps@ 120 volts (single phase).
To put it plainly, If the two single phase "hots" from the generator go through a 100 amp 240 volt breaker before the transfer switch, I should be good.
Does this sound reasonable to anybody here?
Thanks.