The OP did provide a diagram.it would be good to know
engine rated kw/hp
how the windings are actually configured
The OP did provide a diagram.it would be good to know
engine rated kw/hp
how the windings are actually configured
we do not know how the machine was derated and rated
for all we know the 120/208 is correct
wired coils in parallel wye and did not use one line/pair
only 2/3 capacity
we do know this
45 kw
1 phase
clearly marked
those machines have a field v adjustment
it could be set at 115/230 which is close to 45 kw at 0.8 pf
it would be good to know
engine rated kw/hp
how the windings are actually configured
Yes, the double delta configured to get 120/240 single phase that was pictured in post 1.The OP did provide a diagram.
The OP did provide a diagram.
At some point he said it was how it was already connected when he acquired the machine.not sure if that is correct for the machine or what he thinks it is and copied from the internet?
At some point he said it was how it was already connected when he acquired the machine.
I thought he did open it up and has verified the connections. If each coil is 120 volts, then he has two connected in series - that will yield 240 with a 120 volt center tap. Other 4 coils are there to sell excess copper and steel I guess.:blink:he 'thinks' that is how it is wired, he has no manual or drawings
I believe the nameplate is correct
45 kw
120/208
1 ph
but who knows without opening up and looking at it
I thought he did open it up and has verified the connections. If each coil is 120 volts, then he has two connected in series - that will yield 240 with a 120 volt center tap. Other 4 coils are there to sell excess copper and steel I guess.:blink:
Which I assume prompted OP to post questions in the first place.the nameplate begs to differ
:thumbsup:
Which I assume prompted OP to post questions in the first place.
My best guess as has been suggested is this generator can be configured in multiple ways, but the nameplate is sort of geared toward one possible connection, yet not everything on the plate seems to go together.
We can speculate til the cows come home. Perhaps we should ask him if he can respond to the question I asked in post #15.not sure if that is correct for the machine or what he thinks it is and copied from the internet?
If you take my suggestion that is based on 230V utilisation from a 240V generator (which is the exact same ratio as 460/480) then no rounding is required for the current, the kW or the kVA.the nameplate is correct imo
I have seen others on the net from the same company stamped 120/240
what we don't know is how the 3 ph was derated: 33%, 40%, 50%???
and how they rounded that: was it 47.2 kw rounded to the nearest 5, ie, 45
If all 12 ends are brought out he can connect it any way he likes. The double delta configuratiiion shown in post #1 would hive 120-0-120 single phase.The problem here as I see it is that the configuration he is seeing would provide 120/240V single phase, BUT the nameplate says 120/208V single phase, then when he looks inside, he sees 6 windings, indicating a 3 phase base design.
If you take my suggestion that is based on 230V utilisation from a 240V generator (which is the exact same ratio as 460/480) then no rounding is required for the current, the kW or the kVA.
You get the exact data that's on the nameplate.
Damn, you gave the solution with that post above! Here are my calcs:
Ouput - 45 kW
Voltage = 115 VAC
3-phase amps = 282.5 amps
But when connected in 1-phase (zigzag configuration), both phases loaded with 22.5 kW each (1/2 of the nameplate rating), the resulting line currents:
L1-N = 244.57 amps @ 0.8 PF;
L2-N = 244.57 amps @ 0.8PF
derated 33% 1 ph
Are you saying a single ph source can't power a reactive load?
nameplate is stamped 1 phase
45 kw / 0.8 / 240 ~ 245 A
200C #8 hook-up wire is good for 124 A
250 even higher 150 range
Well, It looks like you're right. Thank you by the way,
At closer inspection the leads are more like #4's.
I thought they were smaller because I took it apart years age to tighten up the lead connections. I guess they looked smaller to me then.
It has to be a 70.6 kw machine if it were rewired in doubled-up star if it can pull 245 amps in the double delta.
245 amps from two windings =122.5 from a single one.
6 windings pulling 122.5 amps = 735 amps @120v.
735 divided by 3 phases = 245 amps per phase.
Wired in star = 208v @ 245 amps x 1.732 = 88.262KVA
88.262KVA X .8 pf = 70.6KW
The plate reflects the output of the machine with the double delta lead configuration.
I expected the plate to reflect the max potential output of the generator which would be 3 phase.
A dumb assumption, I guess.
I was further confused by the plate stating single phase but listing the voltage as 120/208.
120/208 implies a 3 phase internal connection.
Currently, the machine is single phase but it is incapable of making 208 volts while wired for single phase.
Seems to me the plate should say Amps: 490/245 Volts: 120/240 Phase:1
I think that 208 was a typo.
I did dig myself in a hole saying a single phase machine should only have a PF of 1, that was a dumb thing to say.
Yes, a single phase generator can power an inductive load, sorry.
It's my understanding that most industrial setting generators (especially 3 phase) are rated at .8 pf because they are expected to run mainly inductive loads which on average, are at a .8 pf.
Single phase generators are generally rated at 1.0 pf because they are generally used in household settings where the largest loads are expected to be resistive. Hot water, electric stove, dryer, etc.
This generator is certainly of the industrial class so the .8 pf does make sense. Sorry for sounding like a dimwit.
Actually, I don't understand why generators are rated in a specific power factor at all. The load makes the power factor, not the generator. If I use this 45 KW generator to run nothing but electric heat and light bulbs, wouldn't I have a 56.25KW generator?