The circuit in question is a generator exciter DC circuit, it is currently 600A fused protected and averages about 460A. The existing conductors are cu quad 250?s RHW-2 (1000 kcmil), 100 feet long bundled in tray and 20% conduit.
I was originally told the overcurrent protection was 500A, with this I come up with 900 mcm for tri 300?s. The engineer is actually saying parallel 4/0?s can be used; wow only 423,200 CM?s! I don?t even know why he would want to downsize? He did send supporting information for this but this information is referencing table 310-17; we are installing DLO type cable (diesel locomotive) but certainly not in free-air application.
As it unfolded we actually purchased DLO type RHW-2 cable 313,000 CM?s and now that I know it has 600A protection I see I can use quad 313?s to achieve 1,250,000 CM?s (derating 70% for bundling in tray and 7-9 conductors in conduit), any less than this would be erroneously protected according to NEC.
So it is my opinion the circuit conductors are greatly undersized and this caused me to wonder about resistance, writing this I can see I may have voltage drop but I don?t know it is an exciter? I would think with the actual 460A load he would need 750 mcm?s at least but again these would be incorrectly protected.
I got a feeling the current will be felt on the conductor bends as well as heat. With all this said I wonder what the outcome would be if in fact the engineer got his desired conductor size of parallel 4/0?s? or even 600 mcm?