Re: Ampmeter Wiring
Think of it this way, An ammeter is basically a shunt in itself, a short circuit so to speak. A CT generates current in its secondary winging in proportion to the current flowing in the primary.
The current can only flow in the secondary circuit in a specified proportion to that which is flowing in the primary if the secondary flow is unrestricted, that is that there is no resistance. Thus, if you were to try to measure the voltage in the secondary circuit which commonly includes and ammeter, you would read '0' volts.
Simply opening that circuit at any point, such as removing a lead from the CT or the Ammeter, will allow a voltage to develop across the open circuit when current is flowing through the primary of the CT, a voltage that could be quite dangerous. The question then would be how high would that voltage be? If one were to consider a 4:1 CT is it possible to induct 4x the primary voltage into the secondary, i.e. 480x4=1920v? Is it possible to exceed the common 600v rated insulation of the CT wire and cause if to fail?That's why it is imperative to short the wiring from the CT or the CT itself when servicing thew CY circuit and its components when there is current flowing through the circuit being monitored, this also includes protective relaying such as common CO relays.