I took it into the restroom where there is a GFCI receptacle, and it didn?t have a ground either. Pressing the test button did not trip anything, since there was no connection to the ground prong.
Any thoughts?
Yes, the test button worked. But then I remember a few years ago that if the receptacle was misconnected with the line on the load side that the test button would trip it, but it did not (obviously) provide protection for anything plugged in.
And, until then, there is no line-to-chassis hazard.Then I think it is just a non grounded system and the designer knew the GFIs would become fucntional
as soon as either line 1 or line 2 of the transformer contacted the Amkrak chassic or metal frame.
I believe that to be correct. The GFCI does not care which conductor is grounded, only that one is.I"ve not tried this on the bench but I believe it will make the GFI recpt. functional if ether line 1 or line 2 get grounded.![]()
a Certified
Electrical Engineer