cbaman
- Berlin, MA
Thank you very much Dereck. I appreciate the opportunity to have a discussion with the forum members on these issues.dereckbc said:I have re-opened for discussion.
Paul
George,georgestolz said:I believe this is something better aimed toward the UL.
George (and Ryan from another post),georgestolz said:1 second is 60 cycles, correct? What's wrong with one second? Or four? It's for protection of equipment, not personnel...?
cbaman said:I have heard many concerns expressed here and on other forums about the length of branch circuits (and the resulting voltage drop at outlets) in some of the large homes being wired today. The underlying problem that I hear with these concerns is that we lack sufficient information with which to make an sound decision. These two proposals will fully address this problem.
Paul
Bob,iwire said:You lost me Don, it sounds to me like the proposal would add a performance requirement.
Compliance with 250.4(A)(5).iwire said:Address what problem?
cbaman said:Compliance with 250.4(A)(5).
No change in sales here...just a change in the performace requirements for breakers that are already required to be installed by the NEC.All that aside I still wonder if the real motive here is sales just like the AFCI section.
don_resqcapt19 said:Bob,
No change in sales here...just a change in the performance requirements for breakers that are already required to be installed by the NEC.
Don
I want to specify certain product performance requirements in the NEC so that the NEC user understands what performance is expected and to achieve compliance with 250.4(A)(5).iwire said:You appear to want to do the reverse...make a code change and then see if the results justify the costs of the change.
Cost of the change is neglible. The proposed changes are current practice for 3 of 4 manufacturers. One would have to make an adjustment to its present trip settings.iwire said:Obviously any reduction in fires is a good thing but all code issues have a cost vs benefit that should be considered.
Bob, I'm 58 years old and have been a practicing service electrician for 30 years. 20 years ago I began pursuing the problem of why some circuit breakers do not seem to respond quickly to shorts or ground-faults. Finally, after 10 years of development in my spare time, I finally introduced the first tester capable of safely conducting an in-situ field test of the short-circuit response of an installed circuit breaker. That is the technology that I have developed and patented. 3 years after its introduction, I still feed my family with my electrical service work that I continue to do full-time, as I also continue to refine the technology that I have worked so long and diligently to develop.iwire said:All that aside I still wonder if the real motive here is sales just like the AFCI section
In 2005 the NEC accepted 2 new articles, 250.4(A)(5) and a new definition for an Effective Ground-Fault Current Path in 250.2. I have produced field test results that document that this requirement is not being met in almost 60% of the outlets in a sample of more than 1000 tests. I'm not running you in circles. There is a compliance issue here that involves circuit breaker performance.iwire said:Please do not run me around in circles.
Clearing a short-circuit or a ground-fault as rapidly as possible is just common sense to me. Why would anyone want such a condition to remain energized any longer than necessary?iwire said:Can you show that a faster breaker response is going to reduce electrical fires?
You seem to think that the only thing I'm trying to address is fires. Not so. I'm trying to point out that if you want circuit breakers to clear faults quickly, for whatever reasons, then I have outlined certain steps that need to be taken to achieve that. If you're happy with circuit breakers staying in thermal mode in response to short-circuits or ground-faults and taking up to several seconds to clear fault currents of 100-600 amps (fault current that just might be sparking), then you would see no value in this proposal.iwire said:Could you later show that reducing VD will reduce electrical fires?
No one has done the research that provides the answers we seek. Until the research proves otherwise, I believe we should take the safest approach to the problem of what starts fires.iwire said:That is what it should take to change or add to the NEC. Not assumptions based on questionable data.
cbaman said:Do you see any requirement to test circuit breakers in either of these proposals?
There are a number of testers that cost 1/4 or less than breaker tester that can test for voltage drop. If that would be a code rule, I don't see it driving the sales of the breaker tester.As far as the second proposal there is more sales to be had.
Bob, I can't find where it says that this proposal is outside the stated boundaries of the NEC. I see in 90.1(B) Adequacy. the statement, "This Code contains provisions that are considered necessary for safety." Proposal 10-55 is to standardize the short-circuit response of circuit breakers with the objective of improving protection from fault current, clearly about safety. I don't see any prohibition anywhere in Article 90 that would preclude this proposal. If you are referring to some other specific language that places this outside the jurisdiction of the Code, please point that language out.iwire said:As far as the first proposal I don't see any issue other than it is IMO outside the stated boundaries of the NEC.
Don
cbaman said:Bob, I can't find where it says that this proposal is outside the stated boundaries of the NEC. I see in 90.1(B) Adequacy.
This proposal would not cost anyone anything. The proposed measures are current practice for 3 of 5 major lines. Two would have to adjust a setting at the factory.Bob NH said:It is always possible to find ways to spend money to improve life safety.
Read 250.4(A)(5). CMP-5 thinks that not clearing ground-faults quickly is a real problem.Bob NH said:The NEC should stick to solving real problems.
This proposal does not specify how a manufacturer should produce a product; it merely specifies what performance is required, not how it should be accomplished. That's product design, and that's up to them. You're confusing performance specifications with product design. They are not the same.iwire said:I see in 90.1(C) Intention. This Code is not intended as a design specification or an instruction manual for untrained persons.
If specifying how a breaker manufacturer produces their products is not a design specification I do not know what is.
This point is difficult to challenge. I agree, this statement seems to limit the scope of the NEC solely to the installation of products, yet chapters 3 and 4 are all about specifying what the NEC wants to see in product requirements. I will ask someone at the NFPA for a comment.iwire said:I see in 90.2 Scope.(A) Covered. This Code covers the installation of....The construction and design of a breaker is not the installation of a breaker.