Maybe not. A 208V L-L insulation system may not necessarily be adequate for an equal L-N amount (this is the problem of slash rated breakers).The OP said it's the service panel, not an ATS, so there are no active components.
Electrically, the high leg voltage is within the panel's actual, if not printed rating.
Where are you getting that it is an ATS?An ATS can be service equipment.
The catalog number ends in ATS. But that could be coincidence.Where are you getting that it is an ATS?
Yes it's a coincidence. A is the code for tin plated aluminum bus, T is for top feed, S is for surface mounting.The catalog number ends in ATS. But that could be coincidence.
I know Square D will mark custom ordered panel with 208/120. Most panelboards I have purchased were assembled on site with stock items though. Those stock items are labeled 120/240. "Load centers" are also labeled 120/240. 120/240 labeled panels can be used on 208 volt wye systems though.By the look of it, not okay per the label.
This appears to be a custom order ATS? I'll defer to anyone who knows more about Siemens ATS, but I wonder who made the mistake:
- the person who ordered the equipment didn't tell Siemens it was high leg
- the Siemens person who designed or labeled it got it wrong
- someone changed the service afterwards
- something else?
One further wonders if Siemens would actually have a different design for high-leg, and therefore whether it's a real safety issue or just a legal one. Many 3 phase panelboards are rated for 240/120 high leg as well as 208/120. But an ATS has more components that might need to be different.
And FWIW, the topic of 240 vs 208 load centers came up a while back, and I did some digging and could not find an instance of one being rated for one voltage system but not the other. They were all approved for both according to my research.I know Square D will mark custom ordered panel with 208/120. Most panelboards I have purchased were assembled on site with stock items though. Those stock items are labeled 120/240. "Load centers" are also labeled 120/240. 120/240 labeled panels can be used on 208 volt wye systems though.
They are likely built with all the same components, would cost more to stock separate panel bus segments for 208 and 240 when the requirements for them would be so similar. Just the fact it is a factory order they can label it to match the application where stuff made for general stock they are going to label for max volts.Great answers everyone! The model number does specifically request for 208/120 per Siemens info. I did also find out that it is also rated for 240/120 as many of you has expressed. But of course since it is technically custom built, there could be parts that are not rated correctly. There is liability in cases like this if information is a little vague. For this particular project it is not going to matter anyways since im going to have to upgrade the panel and cabling with higher amperage because of the new load that is going to be added to this building. I appreciate everyone answers!!
But that would mean that you could only use 2/3 of the breaker spaces, wouldn't it?Even a single phase application has three 600 volt buses in it you just don't use one of them.
I believe so if it is a 240/120 3 phase delta system.But that would mean that you could only use 2/3 of the breaker spaces, wouldn't it?
It seems to me that if you were to use a three phase panel on a single phase service, a third of the breaker landing points would be on a dead bus.I believe so if it is a 240/120 3 phase delta system.
It depends on the panel. While losd centers have limited optiond, there are some panels whuch can have their 'breaker to bus' connections moved so the high leg is not available without loosing breaker mounting space.It seems to me that if you were to use a three phase panel on a single phase service, a third of the breaker landing points would be on a dead bus.
For I-line panels, single and two pole breakers are available with different phase connections so I don't think you would lose any space.But that would mean that you could only use 2/3 of the breaker spaces, wouldn't it?
Not with I-Line series panels. You do have to make sure you order breakers with jaws placed to connect to the two buses you are utilizing though.But that would mean that you could only use 2/3 of the breaker spaces, wouldn't it?