We have recently found that when we run a new 480V motor from a VFD were are seeing a distortion on a nearby analog signal. These particualr shielded analog cables although run in seperate conduit do pass through a pull box that has the 480V motor feeders in it. This pull box is only a couple of feet. There is also a couple off feet inside the drive enclosure where these two cables are in the same proximity?
I would appear that the distortion on the analog signals is being caused by the VFD ouput on the motor cables. My quesion is though since these two different cables are only in the same proximity for a couple of feet in two places is this enough to cause this distortion with this minimal exposure? Whay type of coupling could be occuring here?
Secondly, besides seperating these cables at these locations, is there anything else that can be done to eliminate this noise on the analog input? Are there additional circuit technicques that can be used to get rid of this noise?