conduit and tubing fill tables
got in an arguement the other day about how many wires are allowed in a conduit
I say annex c tables tell you how many of what size of what kind of wires are allowed in which type of conduit. with no derating
the other guy says you have to derate the wires for longer runs and can not pull the max allowed in the conduit.
if you already have determined the size needed for Voltage drop,amp of circuit and all other considerations that the number listed in the tables is what you can pull into the conduits.
am I missing something somewhere?
got in an arguement the other day about how many wires are allowed in a conduit
I say annex c tables tell you how many of what size of what kind of wires are allowed in which type of conduit. with no derating
the other guy says you have to derate the wires for longer runs and can not pull the max allowed in the conduit.
if you already have determined the size needed for Voltage drop,amp of circuit and all other considerations that the number listed in the tables is what you can pull into the conduits.
am I missing something somewhere?