- Connecticut
- Engineer
Is it not to account for the amount of heat generated for overloads and additional ampacity required to prevent thermal damage to the insulation?
Sorry I missed this while reading the thread on my phone.
The load could potentially be 136A for overload.
The additional 25% doesn't have anything to do with overload. I has to do with continuous load. The additional 25% creates a larger termination size to help dissipate the heat from the portion of the load that is continuous.
In Example D3(a), the load is 119A. 51A of the load will be non-continuous and 68A of the load will be continuous. But together, the maximum load will be 119A. According to the load calculation, the highest current the feeder conductors will see is 119A, not 136A.
So the 2/0 conductor has an ampacity of 131A and will carry a load of 119A. It's operating temperature will not exceed it's insulation rating. And the 150A c/b will carry a load of 119A. It will not exceed it's rating. And the 2/0 lugs on the c/b can carry 175A without exceeding its temperature rating, but will only be carrying 119A. So the terminations will not exceed it's temperature rating either.