Annex not a part of NEC

Status
Not open for further replies.

Twoskinsoneman

Senior Member
Location
West Virginia, USA NEC: 2020
Occupation
Facility Senior Electrician
Happen to see this while reading the NEC.
"Annex C Conduit and Tubing Fill Tables for Conductors and Fixture Wires of the Same Size.
This annex is not a part of the requirements of this NFPA document but is included for informational purposes only."
Would you think a juristiction has to specifically mention the adoption of the annexes? Also beside these annexes where else does the NEC give guidline for conduit fill?
 
Twoskinsoneman said:
Would you think a juristiction has to specifically mention the adoption of the annexes?

I don't think any area adopts the annexes, they where not meant to be code.

Also beside these annexes where else does the NEC give guidline for conduit fill?

3XX.22 of each raceway article covers conductor fill and sends you to Table 1 Chapter 9 which is part of the code.
 
Twoskinsoneman said:
. . . This annex is not a part of the requirements of this NFPA document but is included for informational purposes only. . .
Fine print notes and the index are also not part of the NEC. :)
 
Status
Not open for further replies.
Top