petersonra
Senior Member
- Location
- Northern illinois
- Occupation
- engineer
It looks to me like the SS box is being used mostly to hide some work as opposed to a junction box. If that is the case, I don't see a problem, if everything esle is OK.
The SS box (regardless of its usage) appears to be within the 10' bubble (5' radius) around the vent's opening, and therefore within the C1D1 area?a 501.10(A)(3) violation. Possibly true of the LB's too.It looks to me like the SS box is being used mostly to hide some work as opposed to a junction box. If that is the case, I don't see a problem, if everything esle is OK.
The SS box (regardless of its usage) appears to be within the 10' bubble (5' radius) around the vent's opening, and therefore within the C1D1 area—a 501.10(A)(3) violation. Possibly true of the LB's too.
(3) Boxes and Fittings. All boxes and fittings shall be approved for Class I, Division 1.
How the box is used does make a difference, of course. In Class I, Division 1, what must be considered is whether the box can collect ignitable vapors and if there is a potential electrical ignition source inside.Interesting. It never occurred to me that an electrical box not being used as an electrical box would still have to meet this requirement.
I have seen some installations where they do this kind of thing to enclose sampling stations and such to keep it out of the weather.
I have even seen GP electrical boxes used for storage in div 1 areas. Are you suggesting that is not a permitted use?
Would this apply as well to sound enclosures around equipment in Div 1 areas? Those are boxes.
I guess the word "approved" would be key.
My comment was under the context of what I believe the box's usage to be. Apparently you see the box's usage as something non-electrical, while I seem to recall the OP'er mentioning it was a junction box...Interesting. It never occurred to me that an electrical box not being used as an electrical box would still have to meet this requirement.
...
I'm sorry, I've reread this post a half-dozen times to attempt to picture the installation, but I haven't been able to get past the "two 4x plastic boxes" and "cords" in a Class I, Division 1 area.