While we are on the topic, the terminology of bonding/grounding bushing vs bonding/grounding locknut is often swapped around. UL says that a a grounding bushing/locknut has the wire lug, while the bonding bushing/locknut doesn't. In reality many in the trade and some manufacturers call the bushing with the wire lug a "grounding bushing" and the locknut without the lug a "grounding locknut. Here's what UL says:
Grounding and Bonding Bushings — Bonding bushings for use with conduit fittings, tubing (EMT) fittings, threaded rigid metal and intermediate metal conduit, or unthreaded rigid metal and intermediate metal conduit are provided with means (usually one or more set screws) for reliably bonding the bushing (and the conduit on which it is attached) to the metal equipment enclosure or box. They provide the electrical continuity required by the NEC at service equipment and for circuits rated over 250V. Means for connecting a grounding or bonding conductor are not provided and if there is need for such a conductor a grounding bushing should be used.
Grounding bushings for use with conduit fittings, tubing (EMT) fittings, threaded rigid metal and intermediate metal conduit, or unthreaded rigid metal and intermediate metal conduit have provision for the connection of a bonding or grounding wire or have means for mounting a wire connector available from the manufacturer. Such a bushing may also have means (usually one or more set screws) for reliably bonding the bushing to the metal equipment enclosure or box in the same manner that this is accomplished by a bonding bushing. Grounding bushings provide the electrical continuity required by the NEC at service equipment and for circuits rated over 250 V. They may be used with or without a bonding or grounding conductor as determined by the bonding or grounding function that is intended to be accomplished. Insulating throat liners in grounding or bonding bushings are suitable for temperatures of 150°C if they are black or brown in color. Unless otherwise marked, insulating throat liners of any other color are suitable for temperatures of 90°C.
Grounding and Bonding Locknuts — Grounding and bonding locknuts serve in a manner similar to grounding and bonding bushings except they do not provide abrasion protection for the conductor at the end of the conduit.