I have a corner grounded Delta question similar to the existing post but I thought I'd start a new one as not to hijack the other.
I have a brand new 4.16kV Delta to 480V Delta transformer being used as an step down / isolation transformer for a 480V VFD. For both the delta windings the namplate of the transformer shows a dotted line coming from the bottom left and corner of the delta and stopping in the middle of the transformer. I'm not sure what this line means? Does it mean the transformer is corner grounded or does it mean it has the option to be corner grounded?
I also noticed when meggering this new unit that on the secondary all three legs had a very high resistance to ground. I confirmed this with a meter, that there was not continuity to ground on any phases. This tells me that the unit is not corner grounded or else I would have seen a short to ground when performing these tests. I always thought that the winding internally would be tied to ground but it now looks like it is up to the customer to create this corner ground?
Looking at the other post is seems like I need to take a bonding jumper from the "B" phase busbar on the secondary of the transformer and bond this to the transformer frame which is tied into the ground grid as well as high side EGC? Is the correct method of corner grounding this unit?
I have a brand new 4.16kV Delta to 480V Delta transformer being used as an step down / isolation transformer for a 480V VFD. For both the delta windings the namplate of the transformer shows a dotted line coming from the bottom left and corner of the delta and stopping in the middle of the transformer. I'm not sure what this line means? Does it mean the transformer is corner grounded or does it mean it has the option to be corner grounded?
I also noticed when meggering this new unit that on the secondary all three legs had a very high resistance to ground. I confirmed this with a meter, that there was not continuity to ground on any phases. This tells me that the unit is not corner grounded or else I would have seen a short to ground when performing these tests. I always thought that the winding internally would be tied to ground but it now looks like it is up to the customer to create this corner ground?
Looking at the other post is seems like I need to take a bonding jumper from the "B" phase busbar on the secondary of the transformer and bond this to the transformer frame which is tied into the ground grid as well as high side EGC? Is the correct method of corner grounding this unit?