AHJ is requiring us to install emergency lighting in a classroom at a school. I'm not sure that the IBC requires it, but I'm not fighting that. The building has a generator. The owner wants to switch the one emergency fixture with the rest of the fixtures in the space (makes sense). Normally I would use a Bodine GTD or similar, but having re-read NEC 700, 700.25 doesn't seem to allow the transfer from normal to emergency power at the fixture. I've also found that the spec sheet for the GTD is a dead link on Bodine's Website (maybe a coincidence). I was told to look at using an IOTA ETS. This device powers the fixture from the emergency circuit and never the normal circuit, and will allow you to bypass the switch input, but it looks like I'll need a separate switch just for this one emergency light.
How are you guys handling instances where there is just one emergency fixture in a space?
Sorry for the lengthy post, thanks.
How are you guys handling instances where there is just one emergency fixture in a space?
Sorry for the lengthy post, thanks.