I received some more info on this topic from PGMA.
UL?s 2010 version of the White Book reflects what is written in UL standards, which includes UL 2201 (Portable Engine-Generator Assemblies). UL 2201 requires that portable generators must bond the neutral conductors to the generator frame.
The problem is that UL 2201 is a "private" standard and NOT a national (ANSI) standard. Since UL 2201 was published in 2009, I am not aware of ANY manufacturers that have listed products to UL 2201.
There is no ANSI standard that requires a bonded-neutral generator. Therefore, installing a "floating neutral" portable generator as a non-separately derived system, using a two-pole transfer switch, is perfectly acceptable.
I asked the following questions and received these answers (in blue)
I'll keep hunting for more info on this. :thumbsup:
UL?s 2010 version of the White Book reflects what is written in UL standards, which includes UL 2201 (Portable Engine-Generator Assemblies). UL 2201 requires that portable generators must bond the neutral conductors to the generator frame.
The problem is that UL 2201 is a "private" standard and NOT a national (ANSI) standard. Since UL 2201 was published in 2009, I am not aware of ANY manufacturers that have listed products to UL 2201.
There is no ANSI standard that requires a bonded-neutral generator. Therefore, installing a "floating neutral" portable generator as a non-separately derived system, using a two-pole transfer switch, is perfectly acceptable.
I asked the following questions and received these answers (in blue)
- Since there is no ANSI standard requiring manufacturers to fabricate portable units with neutral-to-frame bonding why do they come shipped as such ? Is the assumption that they are going to be used in the field and not connected to premise wiring ?
Not all portable generators are bonded neutral. In the U.S., approximately half of all portable generators sold are bonded neutral and half are floating neutral
- Is there any danger in using the portable with the neutral-to-frame bonding in place when connected to premise wiring ?
For portable generators with a bonded neutral, I think you have to either remove the bond or connect it as a separately derived system (3 pole transfer switch) in order to comply with NEC.
- Is it acceptable and would there be any danger in disconnecting that bond when connected to residential premise wiring ? Any of the units I've used have no instructions to break that bond when used this way.
You would have to contact the manufacturer for an answer to that question
- Are the manufacturers required to provide a simple means to disconnect that bond when used in this way ?
Not that I am aware of.
I'll keep hunting for more info on this. :thumbsup: