Moving a 30kw genset from one location to another. Today I was removing all the old wireing getting ready to rewire when I noticed something I am not sure of. Here is my set up I am feeding the utility connection on transfer switch from a 100amp breaker in the MDP, 100amp breaker in genset is connected to a disconnect and then to the emergy. connection, line side feeds a new panel that will have the selected branch circ. needed for operation of the building. The neutrals are all tied together in the transfer switch ( no switching of the neutrals) On the gen. the neutral and EGC were tied together along with the GEC. I am thinking the neutral and ground should be separate on the genset. But looking at it no mater where you would land the EGC it would still be bonded with the neutral. Neutral buss solid to armature frame, frame bolted to housing, etc....
DOI inspector also wanted a G rod at genset. Am I over thinking this? I have the neutral and ground separate in the disconnect. the neutral and ground are separate in trans. switch And I have the neutral and ground separate in new panel