This job is about a 100 mile round trip, so I am looking for some valuable input. I would like to solve this issue in one trip as I don't plan to charge.
Here is the deal: No room for a GFCI outlet serving counter-top. Installed GFCI breaker instead. Breaker trips from time to time. There seems to be no pattern and it is assumed that it is a ground fault problem as no tripping problem occurred prior to GFCI installation.
The 'GC' is the HO's sister. GC says that there are no other outlets on the breaker except the counter-top. GFCI trips even when all loads (according to GC) are removed from circuit.
I have already tried to verify the problem but could not, as during the last several hour visit the GFCI never tripped once.
So......
Do I use the shotgun approach and replace the GFCI breaker based upon suspicion alone? If there were know issues with the breakers I would not hesitate to use that approach. If that approach is wrong, I won't know until I am back home and another visit will be required.
Do I trust the GC that there are no other outlets and fire up the ol' megger? What if he is wrong and I cook something? Some electronics go into a sleep mode that won't present a visible reading on an ohmeter, thus rendering them 'invisible' to the first step of conductor testing. I am always hesitant to do insulation tests on existing structures, especially older ones.
I would much rather figure out a way to actually verify the problem. I suspect that something is causing a perfectly good breaker to trip and I am not getting an accurate condition report from the GC.
What would be the first thing to look for in my case?
As far as I can see, there is no damage to the Romex which appears to be a very short run from the panel straight up to the outlet box. The box is also used as a J box for a lighting circuit and there is a switch for that circuit in the same box. I have pulled the receptacle and re-positioned the wires to no avail.
If this project was close by I wouldn't even bother you all with my questions. I know I can figure it out, it's just that since I am dealing with an intermittent problem I likely can't do it in one visit.
The GC just wants to put the original breaker (non-GFCI) back in service. Obviously, I declined and am dedicated to solving the problem correctly.
Any insight or info will be useful, thanks!
Here is the deal: No room for a GFCI outlet serving counter-top. Installed GFCI breaker instead. Breaker trips from time to time. There seems to be no pattern and it is assumed that it is a ground fault problem as no tripping problem occurred prior to GFCI installation.
The 'GC' is the HO's sister. GC says that there are no other outlets on the breaker except the counter-top. GFCI trips even when all loads (according to GC) are removed from circuit.
I have already tried to verify the problem but could not, as during the last several hour visit the GFCI never tripped once.
So......
Do I use the shotgun approach and replace the GFCI breaker based upon suspicion alone? If there were know issues with the breakers I would not hesitate to use that approach. If that approach is wrong, I won't know until I am back home and another visit will be required.
Do I trust the GC that there are no other outlets and fire up the ol' megger? What if he is wrong and I cook something? Some electronics go into a sleep mode that won't present a visible reading on an ohmeter, thus rendering them 'invisible' to the first step of conductor testing. I am always hesitant to do insulation tests on existing structures, especially older ones.
I would much rather figure out a way to actually verify the problem. I suspect that something is causing a perfectly good breaker to trip and I am not getting an accurate condition report from the GC.
What would be the first thing to look for in my case?
As far as I can see, there is no damage to the Romex which appears to be a very short run from the panel straight up to the outlet box. The box is also used as a J box for a lighting circuit and there is a switch for that circuit in the same box. I have pulled the receptacle and re-positioned the wires to no avail.
If this project was close by I wouldn't even bother you all with my questions. I know I can figure it out, it's just that since I am dealing with an intermittent problem I likely can't do it in one visit.
The GC just wants to put the original breaker (non-GFCI) back in service. Obviously, I declined and am dedicated to solving the problem correctly.
Any insight or info will be useful, thanks!