Phil,
What a great question!
That's right on the edge of my recollection back from the days of being a wee little Spark. And it's something, as an apprentice, that I didn't pay much attention to ("Yes, Master, I'll do whatever you tell me. . .").
But the answer to your question surprised me. The change happened in the 1968 NEC.
I apprenticed and first tested under the 1965 NEC. Pulling the book from the shelf yields the following (and, parenthetic, I add, to my surprise):
1965 NEC 210.22 Receptacle Outlets Required.
(b) Dwelling Type Occupancies. . .At least one outlet shall be installed for the laundry.
And:
1965 NEC 220.3 Branch Circuits Required
(a) Lighting and Appliance Circuits.. . .<This is the 3 W/Ft? section - Al>
(b) Receptacle Circuits, Dwelling Occupancies. . .<No mention of Laundry - Al>
(C) Other Circuits. For specific loads not otherwise provided for in Section 220-3(a or b), branch circuits shall be as required by other sections of the Code.
That got into whether the wash machine and/or gas clothes dryer were "fixed, portable or stationary" and what the nameplate ratings of the motors were. As I read and recall this, if the washer was something like an Easy Spin Dryer (which was a rolling open tub with agitator, roller to squeeze wash water out, and a separate spinner tub that cetrifugally extracted more water, finally preparing the clothes to be line hung to dry), then the appliance was portable. The motor drew less than 7.5 Amps so it was just another "general lighting load" as we'd think of it now, but with the curious quirk of needing 1500 watts added to the service calculation because there was a "laundry receptacle" (NOTE - not "laundry circuit" )
Things were changing, bigger modern wash machines that were "fixed appliances" were becoming popular. So in the 1968 NEC we see:
1968 NEC 210.22 Receptacle Outlets Required.
(b) Dwelling Type Occupancies. . .<This is unchanged - Al>
But a new sentence was added to:
1968 NEC 220.3 Branch Circuits Required
(a) Lighting and Appliance Circuits.. . .<This is the 3 W/Ft? section - Al>
(b) Receptacle Circuits, Dwelling Occupancies. . .At least one 20-ampere branch circuit shall be provided for laundry receptacle(s) required in Section 210-22(b).
(C) Other Circuits. . . .<This is unchanged - Al>
So, given the Local Jurisdiction's adoption of the NEC into law that the local AHJ can enforce, and when your original wireman pulled the permit, it sounds like your house was probably wired originally to the 1965 NEC.
Does the time line look like it would fit with the history you know about your house?