Normally the fluctuations in the L-L voltages shouldn’t affect the 240V loads, like you stated earlier.
Depending on what single phase loads are trying to start, the line voltages could shift to 0 on one leg and 240 on the other leg.
still shouldn’t bother the compressor.
I agree with you, looks like a board or some other component would be shot, but not a compressor lockup.
i don’t see how the air handler running or not running will cause a compressor to lock up. I can see it controlling the compressor either off or on, but not lock up.
unless...
the board that controls the compressor start delay was shot, and the compressor didn’t get a delay signal... that I could see.
but I thought the board was 24 VAC...
speculation... I’m not an AC guru.
If this is in reference to a Lennox 2 Speed Condensing Unit they are one of the most complicated systems at large, especially the older generation units and there is more than one time delay device on board the outdoor unit that operate under both startup and speed change scenarios. Those units have a 6 lead compressor. I would like to know the " exact " failure on the compressor in order to get an idea. The older generation units were also typically paired with Gas Furnaces indoor which are 120V primary machines, but they could also be set up on full electric heat FCUs which are 240V primary to the control transformer. Typically if you get into a situation where the control voltage is broken to the Furnace, the TDR on the condensing unit will be forced to recycle.
I have to wonder about a stuck contactor or another missing element as something is not quite adding up. The AC guy is apparently casting blame on the failed neutral because it was conincident with the failure. I'd like to hear his explanation based on the mode of failure and how he proposed it happened. The Engineers would have to comment, but if there is a way for the applied voltage to have gone low for an extended period of time when the contactor was engaged, this could do it.