Another Newsletter Article (plan review items)

Status
Not open for further replies.

ryan_618

Senior Member
Ten most commonly missed commercial electrical plan review items

1. For equipment rated over 1200 amperes, two exits from the equipment room are required, unless the conditions of 110.26(C)(2)(a) or (b) is complied with. When the exits are doorways, they must swing in the direction of egress travel, and they must be equipped with panic hardware [110.16(C)(2)].

2. Transformers rated over 112.5 kVA must be installed in a room constructed of at least one-hour fire resistive rated construction. There are two exceptions to this rule, both of which are for transformers with a class 155 or higher insulation system [450.21(B)].

3. All 125 volt 15 and 20A receptacle outlets in commercial kitchens must have GFCI protection. There are no exceptions to this rule, contrary to popular belief [210.8(B)(2)]. Remember that a kitchen is defined as an area with a sink and permanent facilities for both cooking and food preparation.

4. Each commercial building (and each occupancy) must have a dedicated 20A branch circuit for the purposes of installing an electric sign [600.5(A)]. This branch circuit can be used for no other purpose.

5. Each commercial building containing a show window (see Article 100 definition) must have receptacles spaced at intervals not exceeding 12? above the show window [210.62]. These receptacles must be calculated in accordance with 220.14(G).

6. Each panelboard must have a panel schedule that provides enough detail to distinguish each circuit from any other circuit in the building [408.4]

7. Where ungrounded circuit conductors are increased in size for voltage drop, the equipment grounding conductor must be increased in size in direct proportion to the change of size in the ungrounded conductor [250.122(B)].

8. The common installation practice of using the next standard breaker rating (above the ampacity of the conductors) is not permitted for transformer secondary conductors [240.21(C)].

9. Panelboards supplied by a transformer must have a main breaker, or the transformer must have secondary overcurrent protection before the panelboard [408.36(D)].

10. Each building can be served by only one service, unless otherwise permitted by 230.2(A) through (D). When a building is supplied by two services, identification of the location of other service disconnects is required [230.2(E)], and the services must use the same grounding electrode system [250.58].
Ryan Jackson
 
Pierre, I agree with you on #7, but at plan review typically I see this for site lighting, which is indeed for voltage drop.

I haven't had much issue with your other commetn, since 99.9% of the time multioutlet branch circuit are fed with 10 AWG or smaller, and therefore fall under the rules of 240.4(D) for small conductors.
 
For #2, how does one verify a transformer is Class 155 or higher? I don't think they stamp that right on the transformer :?:
 
Actually, the ones I have seen are on the transformer.

I'm still confused about this "Class" business. The shop drawings and cut sheets often don't make it clear if a transformer meets this or not. The last cut sheet I saw for a 100KVA transformer said:

"insulation class 220, 115 deg. C temp. rise."

So is that a "higher" class, or is insulation class something different? If it is a higher class, isn't almost every dry transformer a "Class 155 or higher"?

I had a recent project where we didn't put a transformer in a fire rated room. At first the inpector called us on it. After going back and forth, the inspector decided he couldn't prove the transformer wasn't class 155 or higher. He basically had to give us the benefit of the doubt. Innocent until proven guilty and all that.

The down side is that I still don't know if that was a compliant installation.

Steve
 
Ryan, thanks for the slap upside the head. If asked, I don't believe I'd be able to accurately answer over half of those 'questions.' :shock:
 
Thanks Ryan. So the Insulation Class" is the same as the "Transformer Class".

That info. was from standard dry type Square D transformer. So I'm assuming most standard transformers meet the Class 155 or higher designation. I think one might be hard pressed to find a transformer that doesn't meet the Class 155 or higher. If that's the case, is this really a top 10 violation?

(Again, I could be wrong, I seldom see this info on cut sheets).
 
In my world IG receptacles are a problem.

If I was doing a top ten list, this would definitely be one.

We still have designers calling for a "grounding" conductor to nearest water pipe or bldg steel to an insulated buss in the panelboard, with no Isolated EGC in feeder conduit.
 