Another Odd J-box question

Merry Christmas
Status
Not open for further replies.

rexowner

Senior Member
Location
San Jose, CA
Occupation
Electrician
The question of whether a room could be used as a J-box jogged in my
mind the question:
Can a building be used as the cover plate for a J-box:

PICT0003.jpg


The J-box is for these luminaires:
PICT0005.jpg


What do you think?
 
Last edited:
Rex.,,

only word i say get rid of them and get proper box to support the luminaire [ both luminaire about 8 to 12 lbs a peice ]

for the junction box like that on first photo that is backward set up ughh i am suprised that someone did not get the wire nicked like that.

Merci,Marc
 
rexowner said:
The question of whether a room could be used as a J-box jogged in my
mind the question:
Can a building be used as the cover plate for a J-box:

PICT0003.jpg



What do you think?

Yes, provided it is fed with an indoor wiring method when installed in a damp location, the box is not listed for a damp or wet location, and the raceway connector is not listed for the raceway used. 315.21(A)(3)(c), exceptions 2,4, and 5.
 
frenchelectrican said:
for the junction box like that on first photo that is backward set up ughh i am suprised that someone did not get the wire nicked like that.
Violation of 314.23(B)(1)

Screws shall not be permitted to pass through the box unless exposed threads in the box are protected using approved means to avoid abrasion of conductor insulation.
 
chris kennedy said:
Violation of 314.23(B)(1)

480sparky said:
Using your x-ray vision glasses?​

The picture isn't that good, but indeed the only
visible means of support I observed were what looked like
2 x 2"+ deck screws going through the middle of the box,
so I think Chris has a bingo. Also agree on all the
other comments.

What I found amazing about this installation is that it's
on a storefront on a fairly busy street, and the poor
workmanship is on public display. I took a picture of it
this morning when I was reminded of it by the other
post on J-boxes, but I had been thinking about it in
the vein of the always amusing "spot the violation"
posts. I thought the install was amusing but depressing
at the same time since it seems apparent that anything
goes around here.
 