So I'm replacing a pier panel at a residence. Nothing special, replace in kind. Original one is about 20 years old, rusted out. The homeowner brings out a brand new photocell and asks me to replace the switch for pagoda style lights which are mounted on the pilings. They are protected by a 15 amp gfci breaker which seems to be good. It doesn't trip while switch is operated AND doesn't trip if, with the switch removed, the line and load conductors are temporarily wire nutted together.
BUT as soon as the photocell is installed...connect the neutral to the cell..."click" it trips immediately....even without the load connected. Tried yet another photocell...same exact occurrence. Trips.
So, it trips ONLY when neutral is hooked up.
Operates totally fine with switch or nutted.
Tried multiple photocells, same trip happens.
I searched web and haven't found an answer.
Any idea if just isn't an application where a photocell and a gfi breaker aren't going to work?