Another pool question...
chevyx92
VA BCH, VA
680.26(A) FPN: says the #8 bonding conductor shall not be required to be extended to any remote panelboard or electrode. I get that. Now if you wanted to bond the equipotential grid to a panel, is the #8 REQUIRED to bond it? I say yes it needs to be #8. I did a pool inspection today and saw they had a #12 Thhn from pool motor bond lug to panel next to it as a bond. They also had aluminum railings within 5 Ft. of pool water walls that wasn't bonded. That has to be bonded also right?
did the pool motor have a #8 connected from the pool bonding grid to the lug on the motor? & yes the railings have to be bonded
If you were to attach this panel to the grid # 8 would be rquired... this panel should be more than 5' from the pool though and the hand rail should absolutely be bonded
Courtesy of Mike Holt
Change requires an equipotential bonding grid be installed to reduce voltage gradients in and around permanently installed pools, outdoor spas, and outdoor hot tubs.
(B) Bonded Parts. The following parts of a permanently installed pool, outdoor spa, and outdoor hot tub must be bonded to a equipotential bonding grid of the type specified in 680.26(C).
Author?s Comment: See 680.42(B) for the bonding methods permitted for outdoor spas and hot tubs.
(1) Metallic Parts of Structure. All metallic parts of the water structure, including the reinforcing metal of the permanently installed pool, outdoor spa, and outdoor hot tub shell and deck, must be bonded to the equipotential grid. The usual steel tie wires are considered suitable for bonding the reinforcing steel together for this purpose. Welding or special clamping is not required, but the tie wires must be made tight. Figure 680-4
Where the reinforcing steel of the permanently installed pool, outdoor spa, and outdoor hot tub shell and deck are encapsulated with a nonconductive compound or if it?s not available, an equipotential grid constructed in accordance with 680.26(C) must be installed to mask stray voltage gradients.
(2) Underwater Lighting. All metal forming shells for underwater permanently installed pool, outdoor spa, and outdoor hot tub luminaires and speakers.
(3) Metal Fittings. Metal fittings within or attached to the permanently installed pool, outdoor spa, and outdoor hot tub structure, such as ladders and handrails.
(4) Electrical Equipment. Metal parts of electrical equipment associated with the permanently installed pool, outdoor spa, and outdoor hot tub water circulating system, such as water heaters and pump motors. Accessible metal parts of listed equipment incorporating a system of double insulation and providing a means for grounding internal metal parts are not required to be directly bonded to the equipotential grid.
(5) Metal Wiring Methods and Equipment. Metal-sheathed cables and raceways, metal piping, and all fixed metal parts, as well as metallic surfaces of electrical equipment, must be bonded to the equipotential grid if located:
(1) Within 5 ft horizontally of the inside walls of the permanently installed pool, outdoor spa, and outdoor hot tub, and
(2) Within 12 ft measured vertically above the maximum water level of the permanently installed pool, outdoor spa, and outdoor hot tub, or any observation stands, towers, or platforms or any diving structures.......
mpd said:
what type of pool is it? sounds like you may have problems
It's an inground pool located on the roof of a hotel. All the the pool railings and ladders are bonded. I checked continuity between railings and ladders and ground and they all had good continuity. The motor was my concern as it only had a #12 from the motor housing to the pool pump panel.
you said you inspected this ??? did they use # 12 everywhere ??? Did they bond the rest of it with #8 ??? continuity alone does not a bonding grid make
who's responsibility is it to certify the bonding of a commercial pool in you area chevyx92
Thats the problem I don't if they bonded with #8 because I can't see any. All I went off was my continuity readings. I'm gonna have to double check to see if there is any visible #8. It was dark in there. If they do have #8 bond on all the railings then all they is a #8 bond from motor lug to #8 on the railings to complete the grid right?? And of course bond the aluminum railings with #8 as well.
A master Electrician. We have numerous hotels we do yearly inspections for. This is a new hotel for us. (new for us not new as in hotel) This hotel was built in the late 60's.
if it was built in the 60's unless the bonding was re-done at some point I would bet the pool no longer complies and would need to be renovated as far as bonding
Would it? If it was in compliance then, why isn't it now?
quogueelectric said:
Preexisting Nonconforming. More than 40% reno has to be caught up to current code by me.
You gonna cut the concrete and run #8 to all steel locations and to the pump and light nitch? Gonna attach the bond grid in 4 locations around the deck? Install bond grid within 18" of the walls of the pool?