I'm in favor of installing a mechanical interlock on the main breaker on a panel and backfeeding the entire panel from the generator inlet.
However, I looked at a job where I can't do this and would need to install a subpanel and put an interlock on that.
Someone mentioned to use a gentran. I've seen them but favored the interlock instead.
Researching I see the reliance control panels with individual transfer switches.
I called their tech support asking about the panel not having a main overcurrent protection device in it.
He mentioned they have no issues selling them in the states but when they're installed in Canada they need OC protection.
He mentioned they have an inlet with an installed breaker in it.
Does the (portable) breaker on the generator cover nec requirements for circuit/feeder protection feeding a (installed) panel?
Is it ok to assume that all generators would have a overcurrent device?
Thank you