We have some upcoming systems that will be 1000V ungrounded systems using Power-One Inverters. I'm clear on the fact that we need 1 or 2KV rated PV wire where it's exposed on the roof. I'm also clear on the fact tht USE-2 isn't permitted inside a building unless it's dual rated with a rating that is smoke resistant. So my question is, Can RHW-2 (2KV) be used for 1000V in conduit once it's transitioned from the PV wire in a rooftop J-box?
Also, I'm aware that fine stranded wire can only be used in terminals rated for fine stranding or else you must use a crimp sleeve. What I can't find is anything clearly defining fine stranding. Is that the Class B numbers in Chap 9 Table 10? More specifically if I'm using #10 (19 strand) PV or RHW-2 wire, can I directly connect it to the lugs on load center circuit breakers?
Does anyone have a suggestion about where to find 1000V UL rated terminals for the rooftop wire transition box? The Allen Bradley 1492-J10 terminals that we normally use carry a 600V UL rating and a 1000V IEC rating. Will inspectors accept the IEC rating?
Thanks,
Jeff Schmidt
Also, I'm aware that fine stranded wire can only be used in terminals rated for fine stranding or else you must use a crimp sleeve. What I can't find is anything clearly defining fine stranding. Is that the Class B numbers in Chap 9 Table 10? More specifically if I'm using #10 (19 strand) PV or RHW-2 wire, can I directly connect it to the lugs on load center circuit breakers?
Does anyone have a suggestion about where to find 1000V UL rated terminals for the rooftop wire transition box? The Allen Bradley 1492-J10 terminals that we normally use carry a 600V UL rating and a 1000V IEC rating. Will inspectors accept the IEC rating?
Thanks,