wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
Seems to me that 250.6 is saying "even if other sections say you may do X, if it results in objectionable current, you must remediate it in one of the following ways."Although I think the sections are pretty explicit that you can do the things that cause the supposedly objectionable current which evidently isn't objectionable because you can do those things.
Apparently that is out of date? If up.codes is to be believed, the 2022 SF electrical code says that service entrance conductors shall be limited to the following wiring methods: RMC, IMC, Busways, Auxilliary gutters, PVC, MI, HDPE, NUCC, and RTRC.2) In SF, where I got started, only hard metallic conduit is permitted for service conductors so there's really no way around it.

Chapter 2 Wiring and Protection: San Francisco Electrical Code 2022 | UpCodes
UpCodes offers a consolidated resource of construction and building code grouped by jurisdiction

Cheers, Wayne