Ok, I need some help, I have been looking at this for some time.
I have a 137unit apartment building and having some problems with the Range portion of the calc. Why is the NEC table 220.55 comumn's B and C so far off in my calc?
What in the world did I miss?
The ranges they are using are those small 24" ranges with a load of 8,700VA. If I use column B vs Column C the calc is so far different.
If I read it correctly I can use Column C if I choose even though the load is under 8.75KW?
See Calcs Below
Electric Ranges for a 208Y/120-V, 3-phase, 4-wire system (NEC 220.55 Column B)
Building Voltage 120/208/3
8,700VA per Range
Total Ranges=137
Max Ranges per any 2 Phases = 92
92 Ranges * 8,700 = 800,400VA
Demand Per Table, 800,400VA * .16 = 128,064VA
Per Phase Demand 128,064VA / 2 = 64,032
Equivalent 3-Phase Load = 64,032*3 = 192,096VA
Electric Ranges for a 208Y/120-V, 3-phase, 4-wire system (NEC 220.55 Column C)
Building Voltage 120/208/3
Ranges less than 12,000VA
Total Ranges=137
Max Ranges per any 2 Phases = 92
Demand per table 92 * 750VA = 69,000VA
Demand per table 69,000VA + 25,000VA = 94.400VA
Per Phase Demand 94,000VA / 2 = 47,000
Equivalent 3-Phase Load = 47,000*3 = 141,000VA
So what in the world did I do wrong? Why would using a 12,000VA range vs using a 8,700VA range make the calc that far scewed with the smaller range making for a bigger service.
One would think the larger range would make for a larger service.
If I did my calc right it would not pay to use column B unless the range load is less then about 6,300VA. So I must have a problem someware.
Thanks all
Jay
I have a 137unit apartment building and having some problems with the Range portion of the calc. Why is the NEC table 220.55 comumn's B and C so far off in my calc?
What in the world did I miss?
The ranges they are using are those small 24" ranges with a load of 8,700VA. If I use column B vs Column C the calc is so far different.
If I read it correctly I can use Column C if I choose even though the load is under 8.75KW?
See Calcs Below
Electric Ranges for a 208Y/120-V, 3-phase, 4-wire system (NEC 220.55 Column B)
Building Voltage 120/208/3
8,700VA per Range
Total Ranges=137
Max Ranges per any 2 Phases = 92
92 Ranges * 8,700 = 800,400VA
Demand Per Table, 800,400VA * .16 = 128,064VA
Per Phase Demand 128,064VA / 2 = 64,032
Equivalent 3-Phase Load = 64,032*3 = 192,096VA
Electric Ranges for a 208Y/120-V, 3-phase, 4-wire system (NEC 220.55 Column C)
Building Voltage 120/208/3
Ranges less than 12,000VA
Total Ranges=137
Max Ranges per any 2 Phases = 92
Demand per table 92 * 750VA = 69,000VA
Demand per table 69,000VA + 25,000VA = 94.400VA
Per Phase Demand 94,000VA / 2 = 47,000
Equivalent 3-Phase Load = 47,000*3 = 141,000VA
So what in the world did I do wrong? Why would using a 12,000VA range vs using a 8,700VA range make the calc that far scewed with the smaller range making for a bigger service.
One would think the larger range would make for a larger service.
If I did my calc right it would not pay to use column B unless the range load is less then about 6,300VA. So I must have a problem someware.
Thanks all
Jay