looking for some thoughts, theories, ideas...
1 PH 200A load center fed from POCO pole top transformer - short circuit rating unknown
mcb is 22k AIC
panel feeds parking lot lighting and site lighting only. Pole top transformer feeds approximately 4 stores in the strip mall.
All site lighting runs through contactors that are controlled by a time clock
all branch circuit breakers are 10k AIC and sized properly for the load.
We've megged all the circuits and have 3 runs that indicate a problem
run 1 - H-G 11.01
run 2 - H-G 0.08
run 3 - H-G 0.78
everything else is over 50, with most being >1000
27 poles - approx 20 of them have in-line fuse in the base (the others were removed at one point or another)
ground rods driven at each pole in the base.
approximately 1.5 yrs ago, mcb tripped 3 times in a 2 week span during a heatwave. no lasting problems...no problems since...
2 weeks ago, mcb tripped again...hasn't since...
have been told that the problem could be a short to ground that carries back to the load center, and trips the main in that it basically makes an 'end run' around the branch circuit breakers.
It was my understanding that the branch breakers should trip 1st due to the lower AIC rating?
also was advised that replacing the 200A MCB with a fused disco with TD fuses would eliminate the main from tripping and cause any problem to trip the branch circuit breaker.
not about to start swapping parts for the heck of it, so, i'm trying to grasp what could possibly cause the 200A MCB to trip vs. the branch circuit breakers....
any thoughts? if any of the mods can explain how to post a PDF, i'll post the megger readings
1 PH 200A load center fed from POCO pole top transformer - short circuit rating unknown
mcb is 22k AIC
panel feeds parking lot lighting and site lighting only. Pole top transformer feeds approximately 4 stores in the strip mall.
All site lighting runs through contactors that are controlled by a time clock
all branch circuit breakers are 10k AIC and sized properly for the load.
We've megged all the circuits and have 3 runs that indicate a problem
run 1 - H-G 11.01
run 2 - H-G 0.08
run 3 - H-G 0.78
everything else is over 50, with most being >1000
27 poles - approx 20 of them have in-line fuse in the base (the others were removed at one point or another)
ground rods driven at each pole in the base.
approximately 1.5 yrs ago, mcb tripped 3 times in a 2 week span during a heatwave. no lasting problems...no problems since...
2 weeks ago, mcb tripped again...hasn't since...
have been told that the problem could be a short to ground that carries back to the load center, and trips the main in that it basically makes an 'end run' around the branch circuit breakers.
It was my understanding that the branch breakers should trip 1st due to the lower AIC rating?
also was advised that replacing the 200A MCB with a fused disco with TD fuses would eliminate the main from tripping and cause any problem to trip the branch circuit breaker.
not about to start swapping parts for the heck of it, so, i'm trying to grasp what could possibly cause the 200A MCB to trip vs. the branch circuit breakers....
any thoughts? if any of the mods can explain how to post a PDF, i'll post the megger readings