thank you for your help... I have another question I hope you can solve it >> If two power systems connected in parallel and one power system increase its power output to 100MVA, if the second power system not respond simultaneously to the change, the second system will:
a) increase the frequency b) decrease the frequency c) the voltage will rise d) the freq. not change
If they are connected in parallel they can't run at different frequencies.thank you for your help... I have another question I hope you can solve it >> If two power systems connected in parallel and one power system increase its power output to 100MVA, if the second power system not respond simultaneously to the change, the second system will:
a) increase the frequency b) decrease the frequency c) the voltage will rise d) the freq. not change
If they are connected in parallel they can't run at different frequencies.
I'm afraid your are. Generators or, more correctly alternators, have be synchronised and in phase with the supply the are to be switched into. In the good old days that was sometimes done manually with incandescent lamps showing the difference and the plant attendant would wait for them to stop rotating and be in the 12 o'clock position before closing the breaker. More modern synchronising systems detect it instrumentaly and and allow the breaker to close only when phase and frequency are matched.I dont believe that quite accurate. Perhaps I was taught incorrectly, but when paralleling with the POCO from the plant genset, the genset has to run slightly higher frequency than the grid to 'pick up' the load, and when transferring back, the generator must drop below the grid frequency to transfer the load back to the grid. ofc all of this has to happen in synchronicity lest you want to turn your switchgear into a very expensive fireworks display. and it happens quite quickly (few cycles?). Am I wrong?
If you mean alternators, they are generally, perhaps almost always, synchronous machines. The load angle may change but the frequency does not.2 generators on the same grid will run at different freq after a step load change
this is a short transient period until the controls regulate
If you mean alternators, they are generally, perhaps almost always, synchronous machines. The load angle may change but the frequency does not.
A single autonomous machine may. Not one connected to a system which is what the OP described.I mean a synchronous machine driven as a generator http://xn--drmstrre-64ad.dk/wp-content/wind/miller/windpower web/en/tour/wtrb/syncgen.htm http://www.eecs.ucf.edu/~tomwu/course/eel6208/notes/09 Synchronous Generator and Motor.pdf
the frequency/speed will droop
the governor will compensate
yes it doesA single autonomous machine may. Not one connected to a system which is what the OP described.
Did you miss this?yes it does
see my prior post 17 (interesting article btw)
it describes a large multi-unit grid
fig. 5 shows the 2 units running at different speeds vs load until the controls reach equilibrium (the disturbance in the op's case to upset from equilibrium is a 100 MVA step change)
Did you miss this?
"Governors using speed droop or speed regulation require a sustained change
in system frequency to produce a sustained change in prime mover control"
The machines can't run at different frequencies.
Draw the waverforms and you will see why.