It is not completely clear what the OP described.
But, except for a very short transient period, short enough that the two (or more) sources do not drift far out of phase (certainly less than 1/4 period), the frequency of all units in the interconnected system must be the same.
The nature of current flow between the paralleled generators would be such that the faster unit (leading phase, at least at first) will see a heavier load and the lagging unit will see a lowered load or even a motor drive.
That power balance shifting will have the effect of pulling the units to a common frequency even as the governors are trying to achieve a steady state mutually agreed final frequency.
As noted in the referenced paper, separate elements in the network are responsible for effectively tweaking the governor action to reach the target system frequency and even phase. (For example, long term network performance to maintain the right number of ~60Hz cycles in a 24 hour period.)
But, except for a very short transient period, short enough that the two (or more) sources do not drift far out of phase (certainly less than 1/4 period), the frequency of all units in the interconnected system must be the same.
The nature of current flow between the paralleled generators would be such that the faster unit (leading phase, at least at first) will see a heavier load and the lagging unit will see a lowered load or even a motor drive.
That power balance shifting will have the effect of pulling the units to a common frequency even as the governors are trying to achieve a steady state mutually agreed final frequency.
As noted in the referenced paper, separate elements in the network are responsible for effectively tweaking the governor action to reach the target system frequency and even phase. (For example, long term network performance to maintain the right number of ~60Hz cycles in a 24 hour period.)