When terminating aluminum conductors, there are several practices one should be aware of to ensure a
quality connection that will remain trouble free.
1) Always use a connector that is listed for use with aluminum wire.
2) The following is recommended but not required. Always follow the connector manufacturer’s
instructions
a. The surface of the conductor should be wire-brushed to break any aluminum oxide
barrier leaving a clean surface for the connection.
b. The use of anti-oxidant compound, joint compound, is not required unless the
connector’s manufacturer requires it. However, the use of a listed joint compound is
always a good practice.
3) Always tighten set-screw type connectors to the manufacturer’s recommended torque.
4) Most importantly, do not re-torque the terminations as part of routine maintenance. As
with copper conductors, repeated tightening of any set-screw connections can result in the
eventual “biting” through the conductor causing the termination to fail.