MR. S said:
In Art.320 it states type ac cable needs an insulating bushing (red head)when terminating. No where in Art. 330 does it say an insulating bushing is needed for type MC cable, so we are under the assumption type MC cable does not need a red head at the termination (we use them anyway). Someone brought to our attention Art.300.42. We are in dissagreement over this article. Does 300.42 state an anti-short bushing is needed for MC cable?
If 300.42 existed in a vacuum, then my answer would be
yes the antishort is needed so that "Where conductors emerge from a metal sheath and where protection against ..... physical damage is necessary, the insulation of the conductors shall be protected by a cable sheath terminating device".
But 300.42
doesn't exist in a vacuum. . 320.40 states that AC cable needs to have "an insulating bushing or its equivalent protection shall be provided between the conductors and the armor". . But the same committee wrote 320 + 330 and CMP7 chose not to put that wording in 330.
"Does 300.42 state an anti-short bushing is needed for MC cable?"
My interpretation is that CMP7 has determined that "protection against ..... physical damage is necessary" does not apply to MC cable. . I guess they feel that MC has a magically barrier between the jacket and conductor insulation. . All I've ever seen was a thin clear plastic sheet that installors tear off even with the jacket cut edge.
They don't care if the freshly cut jagged metal jacket edge of MC slices into the insulation. . It's not a code or listing requirement.
But don't confuse code requirement with the concept of "needed".
"No where in Art. 330 does it say an insulating bushing is needed for type MC cable"
It doesn't say it's "required". . It says nothing about need. .
Of course it's needed ! . Why would you want to compress the freshly cut metal jacket edge into the conductor insulation ? . It's not code required but it absolutely is needed. . Don't operate under the assumption that the NEC is always correct !
Determining whether it's NEC required or just needed isn't important to the electrician but it makes a huge difference when you're an inspector. . It sometimes is what causes you to pass an inspection that is of very poor quality.
David