You got a code section for that?Heck, we'd never get anything actually fixed.
We'd spend 3 days just discussing it.
You got a code section for that?Heck, we'd never get anything actually fixed.
We'd spend 3 days just discussing it.
Having small problem with my own residential service. Triped 200 main twice in last 2 weeks. Both times were Saturday nights with heavy loads but far under 200 maybe not even 100 amps. Breaker (SQ D) was hot to touch. Tightened wires and they did need it. POCO dropping line in afternoon to check there lugs. Would like to own a low end meter to help in future . Any suggestions and rough price.
You got a code section for that?
besides your hand, good milk chocolate also makes good thermometer
Can you elaborate?All you need is to do a FALL OF POTENTIAL TEST FOP, what was done prior to hand held IR thermometers.
What he is after is measuring the voltage drop from point to point thru the service. Depending on amount of amps going thru it the service you would see a voltage drop perhaps across the breaker from the in to the out. Very slow way to go about it but in a pinch could find problem.Can you elaborate?
When I think of FOP, I think of testing a grounding electrode system; how would it work for testing bad connections?
I was not really concerned about there wire getting hot. My concern is the main breaker getting hot and triping. A normal load with all my heaters running and other good stuff is about 20 kw in heat assuming all are running non stop , Air conditioner in main house,other loads are harder to add but include hot tub , 4 crock pots on warm, freezer,2 frigs, lights,water heater,water pump, DJ sound system. Rough guess puts me at about 30 kw and some peaks.100127-1427 EST
Jim W in Tampa:
I did a quick check on your voltage drop at 175 A. Looks about correct for the wire length.
Aluminum is 1.65 times copper. 1000 ft copper #2 is 0.156 ohms. Thus, for a loop length of 600 ft the resistance should be about 0.6*1.65*0.156 = 0.154 ohms at 20 deg C. Your test time would not cause an appreciable increase in wire temperature. 34 V drop at 175 A = 0.194 ohms. My pole transformer has an impedance somewhat under 0.06 ohms.
.
How are compensating for emissivity or does it matter?100127-1820 EST
Jim:
The point of my calculation was that the voltage drop you measured was about what could be expected for your wire length.
Prior to your correcting the loose joints you no doubt had a small additional voltage drop. If the voltage drop across the main breaker and its connections was even 1 V, then with your 175 A load on both sides of the main there would be 350 W dissipation. That would be quite hot. Direct measurement of the voltage drops in the main panel would be the best troubleshooting method. But IR is a nice quick way to look for hot spots.
34 V at 175 A is 6000 W dissipation in your service wires and some in the transformer. Somewhat less than 6000 in the wires because of the reactance in the transformer. Just the wires alone maybe 175^2*0.154 = 4716 W.
As an aside using my son's Fluke 62 IR thermometer most spots in my basement are between 66 and 69 deg. Same all over the main panel which is in the basement and near the furnaces and water entry. The outside of my gas water heater is 77 deg. The furnace flue is 220 as it leaves the furnace when heating. The hot air duct is about 88 and drops to 69 during the off part of the cycle. Obviously internal temperatures are higher. It is amazing how well this Fluke works on all different surfaces. My refrigerator freezer reads -10 and 33 in the other part. My solid core front door is 54 and the plate glass beside it 44. My windows with storms are about 55. The outside temperature is about 20. I would recommend this little meter.
.