Was pricing a house and notice the panel was full, and someone added a two circuit subpanel - and quess what - both circuits in the sub were loaded up. This panel is the old Westinghouse that has colored breaker handles - Red is 20 A, Blue is 15A, and I'm not sure what the other Amperages are, but remember a Green one. Electrical supply in town indicates that the Cutler Hammer BR series are the replacements for the Westinghouse.
The panel has 100 A Main, and if memory serves me right - there were three 2-pole breakers and then twelve single pole breakers. There were a set of lugs at the top of the panel - I assume tied directly to the bus. Whomever installed the subpanel, fed off the these lugs. It appears to be #8 AWG feeding between the lugs and the subpanel, which is MLO. And again, the panel only has two breakers.
First question, is this a legal installation as it stands?
The my next question involves taking out the two circuits subpanel and adding an eight circuit. There are several circuit breakers that have two wires in to them, which go off and feed two seperate circuits. The added breakers in the new subpanel will allow the circuits to be split up - and one thing I'll note, is that the total current draw is fine, considering the 100A main. Would this fall under the section in the code (this is kind of what I'm asking as to the first question - is the present installation legal) that covers taps - as far as feeding the new eight circuit panel via the lugs at the top of the panel.
Normally when I've added a subpanel, I've fed them off a two pole breaker in the main panel.
Thanks,
Brett
The panel has 100 A Main, and if memory serves me right - there were three 2-pole breakers and then twelve single pole breakers. There were a set of lugs at the top of the panel - I assume tied directly to the bus. Whomever installed the subpanel, fed off the these lugs. It appears to be #8 AWG feeding between the lugs and the subpanel, which is MLO. And again, the panel only has two breakers.
First question, is this a legal installation as it stands?
The my next question involves taking out the two circuits subpanel and adding an eight circuit. There are several circuit breakers that have two wires in to them, which go off and feed two seperate circuits. The added breakers in the new subpanel will allow the circuits to be split up - and one thing I'll note, is that the total current draw is fine, considering the 100A main. Would this fall under the section in the code (this is kind of what I'm asking as to the first question - is the present installation legal) that covers taps - as far as feeding the new eight circuit panel via the lugs at the top of the panel.
Normally when I've added a subpanel, I've fed them off a two pole breaker in the main panel.
Thanks,
Brett