jwelectric said:
Let?s start with the tap rule
(B) Feeder Taps. Conductors shall be permitted to be tapped, without overcurrent protection at the tap, to a feeder as specified in 240.21(B)(1) through (B)(5). The provisions of 240.4(B) shall not be permitted for tap conductors.
We can tap what? The feeder
The comprehension of this provision actually starts at 368.17(C), which addresses requirements of feeder and branch circuit tapping of a busway?the busbars in the discussion's main panel. In summation it requires an OCPD at the tapping of the busway. However, it goes on to the following ? Exception No. 1: As permitted in 240.21. This relinquishes the requirement for an ocpd at the tapping of the busway, but in no way relinquishes the requirement that the tapping conductors must have overcurrent protection. That is dealt with in 240.21. Note also the tapping conductors are categorized as either feeder or branch circuit conductors.
jwelectric said:
Now let?s look at 409.36 exception 1
Individual protection for a lighting and appliance panelboard shall not be required if the panelboard feeder has overcurrent protection not greater than the rating of the panelboard.
If what has protection? The feeder
You are trying to use the Overcurrent protection for a tap rule to fulfill the requirement for the required feeder protection. The two are different.
No they are not different. The tap conductors ARE the feeder conductors for the panel. Overcurrent protection on a conductor is overcurrent protection regardless of whether it a serves as service, feeder, or branch circuit conductor. Yes, there are some stipulations as to where and how the overcurrent protection must take place in some instances. 408.36 Exception No. 1 has no such stipulations other than the overcurrent protection cannot exceed the rating of the panel. Tap rules achieve overcurrent protection by having an ampacity of not less than the rating of the device supplied (the subpanel) and not less than required to carry the connected load (the panel's branch circuits.
jwelectric said:
Does the feeder being tapped have Overcurrent protection?
Yes, the 100A main breaker.
jwelectric said:
The feeder Overcurrent is what would protect the tap in the event of a ground fault or short circuit...
"Feeder" as you have used here I take to be the busway. Also, I take "tap" to mean the tapped conductors. "The tap" is actually the electrical connection, not the conductors.
Your assessment is incorrect. The busway feeder ocpd protects the busway, and the only the busway. It does not protect the tap conductors.
...and the Overcurrent device that the tap is terminated with protects it from Overcurrent.
If there is an overcurrent device at the termination of the tap conductors. Otherwise, the ampacity of the tap conductors must be "not less than the rating of the device supplied".
jwelectric said:
Protection as outlined in 240.21 is to protect a tap not the feeder that supplies the tap.
"Tap" meaning tap conductors. I have a feeling

you are having a hard time accepting that tap conductors can also be feeders.
Let's clarify this:
1) The busways of the main panel are feeder conductors. They are the tapped feeder.
2) The #6 wires are the subpanel feeder conductors. They are the tapping feeder.
3) Nos. 1 and 2 constitute TWO distinct feeders, each having to meet requirements of overcurrent protection... but with regards only to their particular aspect of power distribution, not as though they are the same feeder. Again we're back to if the tap conductors are required to have an ampacity of 100A, they would not be tap conductors.
There's little point in continuing this discussion unless you agree. I can lead the blind but I can't make 'em see.
I have some errands to take care of now... I'll be back later to see where we stand