Here is a layout I did using very similar SNAC panels, had I mounted them all at 5' as the instructions may have said it would be ridiculously spread out.

Mixed179.jpg


I do have an issue with the carts but that was beyond my control.

LowesWarehamFA.jpg

That is nice install iwire, but it looks like the cabinets are obstructed...!
 
As you mentioned, this is the location indicated on the (approved) plans, and as the inspector had no issue with this location, it is deemed compliant. I would have thought that the AHJ would have had heartburn on that location because they are responding to and interfacing with them during a fire emergency.

Because NFPA 72 lists among others, the NEC as referenced publications, I understood that the required clearances in front of FA panels were the same as electrical panels, and that is how we design/install today.

Personally, I never designed control panels in the cart storage areas. Unlike a locked door that a firefighter can simply remove with an ax, that many carts are a little harder to deal with.
 
Then there are no instructions the NEC requires we follow.

There was a proposals to change 110.3(B) so that it includes all instructions that the manufacturer includes.






And neither do I, I respectfully suggest you try to see things from the outside of your office and what we in the field are up against.

Read the instructions that come with any appliance, many of the words in those instructions have nothing to do with electrical safety.

For example, I install solar panels, the instructions direct that the glass should be cleaned on a regular basis

Am I violating 110.3(B) by not doing so? Is the customer?

Take a look at the instructions that come with a dishwasher, very likely they will say to use specific brand of soap.

It's in the instructions it must be code right?



I think that I need to follow the NEC, (or MEC in my case) that is all I am bound to unless other standards are referenced which brings us back to 110.3(B)



So put that to the picture of the snac panel up high?

There is very little to service in that box, an exhaust fan has more reason for easy access but they are regularly mounted in hard to access locations.

A slippery slope to head down, I will stick with the NEC.



What code section will be placed on that correction notice?

Don't misunderstand me, I think that is a poor location. I work on this stuff all the time, I don't just talk about it. Many times I show up for a service call and I have to reschedule with a lift to access whatever it is. But the NEC is not a design manual, good design comes from good designers not inspectors asking for more then the NEC requires.

FYI..I have been out in the field, talking to folks just like yourself (not just behind a desk):D. My perception is that many don't think they need "those pesky installation instructions" for most of the equipment they install. Usually, they have already read the instructions once, and they remember. But there are a few that don't bother and try to go it alone and do it 'their way'. Thats when things can go bad.

Your analogies illustrating your point about these instructions having nothing to do with electrical safety couldn't be further off the point. If you, as an installer, decide to deviate from the manufacturer's recommended installation guidelines, then you are taking a big chance that the device may not perform as advertised, or could become unsafe at some point in the future. NEC compliant or not, the device can only be guaranteed to work as advertised if the recommended installation is followed.

110.3(B) Is clear. Refer to the listing. I would contend that my excerpts in my previous post could be considered part of the listing as the links to them are directly from the manufacturer's UL Listing certification page. The UL guides take precidence as they clearly state that all manufacturer's installation instructions must be followed.

You may not have a direct NEC violation, but there is an indirect violation of 110.3(B) through UL's guide. IMHO:smile:

The real people to blame for this installation are the architect/designers. They should have read the manual and interpreted the requirements on the specification drawing. If the contractor followed the drawing, they are not technically at fault, and they may have said something.

Not to berate the subject, but it is obvious that we have two very different opinions backed up with documentation. I respect and can see your point of view!:)
 
High ambient temperatures.......

High ambient temperatures.......

This product normally houses (2) 12 volt 7 amp. hour sealed lead acid batteries. As installed, near the roof, high ambient temperatures can lead to premature (sometimes dramatically premature) battery failure. Could even take place during the winter, as the building's heaters create pockets of hot air (which rise) generating temperatures much warmer than one would guess walking on the floor.
 
Last edited:
Not to berate the subject, but it is obvious that we have two very different opinions backed up with documentation.

I can not disagree here, I sometimes find the listing processes frustrating.

A clear example of the listing process gone haywire is 'classified breakers'

A panel label list specific breakers that we must use in that panel per 110.3(B) but now we also can use classified breakers in that panel that are not listed in the labeling. :confused:

Thinks like that really undermine the integrity of the whole process.



I respect and can see your point of view!:)

Right back at you. :cool:
 
In California anyway ? all fire alarm equipment installed is required to be California State Fire Marshal (CSFM) approved, the process of which is similar to getting UL Listed. Although this may not be a requirement in your jurisdiction, the thought process of following the mfr instructions is included in the approval process. The CSFM Listing sheet for this power supply
http://osfm.fire.ca.gov/licensinglistings/pdf/bml/listings/0050/0075-206.pdf states:

?INSTALLATION: In accordance with listee's printed installation instructions, applicable codes and ordinances and in a manner acceptable to the authority having jurisdiction?

Again, while I believe this to be a stupid location, applicable ordinances, and in a manner acceptable to the AHJ appears to be met as the system was (believed to be) approved, even though it could be argued that the mfr instructions were not followed.
 
Yes this is a code violation

Yes this is a code violation

Look at NFPA-72 and tell me that that is 6.5 feet to the top.
You should write this up as a violation (not-accessible) and provide them a quote to relocate. This is a great opportunity to make some money.
 
Last edited by a moderator:
Look at NFPA-72 and tell me that that is 6.5 feet to the top.
You should write this up as a violation (not-accessible) and provide them a quote to relocate. This is a great opportunity to make some money.


You will have to do better then just say 'look at NFPA 72' tell us what code section.

You do realize SNAC panels are not control panels?
 
You will have to do better then just say 'look at NFPA 72' tell us what code section.

You do realize SNAC panels are not control panels?

They are control panels.

They are listed under:

UOXX.S2424
Control Unit Accessories, System

Per the cut sheet:

STANDARDS and CODES
The FCPS-24FS8 complies with the following standards:
? NFPA 72 National Fire Alarm Code.
? UL 864 Standard for Control Units for Fire Alarm Systems
(NAC expander mode).

? UL 1481 Power Supplies for Fire Alarm Systems
(stand-alone mode).
 
OK from the A+E specs:

B. All equipment and components shall be installed in strict compliance with manufacturers' recommendations. Consult the manufacturer's installation manuals for all wiring diagrams, schematics, physical equipment sizes, etc., before beginning system installation.

No, I am not citing a code here, but, if this was a professionally engineered system (which I believe we can agree to) Then this is another standard that would be applied to its installation.
 
I don't have the code cite, but I can find it. NFPA 72 in the fundamentals section I believe says something like “all fire alarm equipment shall be installed per its UL listing and manufacturer's instructions." There is even a section requires non required equipment to be installed to meet the code.
 