Anyone ever get failed for to many wires in a drilled hole?

Status
Not open for further replies.

danickstr

Senior Member
I never have, but i remember someone here saying that drilled holes can only be filled to 60%. I know I have put more than that in them but have never had it brought to my attention buy an inspector.
 

mcclary's electrical

Senior Member
Location
VA
I never have, but i remember someone here saying that drilled holes can only be filled to 60%. I know I have put more than that in them but have never had it brought to my attention buy an inspector.

If more than 2 nm cables are going in a hole to be fire stopped or draft stopped, derating will apply.

If you're not draft stopping or fire stopping, you don't have to worry about it
 

220/221

Senior Member
Location
AZ
They don't fail here.


Seems like if you stuff the hole full of romex, you don't need firestop :grin:
 

mcclary's electrical

Senior Member
Location
VA

I now understand what he meant, I thought he meant derating did not apply,,,,it does apply it just does not affect the breaker size until you get over 9ccc's

EX. 310.16 says 14 is good for 25 amps
334.80 says that if more than two nm cables pass through a hole to be fire stopped, than 310.15 (b) (2) (a)

310.15 b2a says 4-6 CCC derate to 80%=20
7-9 CCC derate to 70% = 17.5

So he's right, I misunderstood him. I thought he meant derating does not apply, it does, but it doesn't affect normal breaker size until you get over 9 CCC
 