They really tried to make the truck look like a cafe or something. The one's we did were the old Ups type vehicles- we called them step vans

There's a lot to be said, mechanically and aesthetically, for a bottom-fed twist-lock inlet. Probably better for water resistance, too.Looks nice, but one addition- an eye-bolt over the the CS inlet, used to tie off a strain-relief rope (otherwise, there's a lot of side load on the receptacle and mounting).
Where is the Neutral to Ground bond? If connected to a generator, some have the bond and some do not.Customer balked at price of conduit, so I ran BX throughout.
Where is the Neutral to Ground bond? If connected to a generator, some have the bond and some do not.