zemingduan
- Philadelphia,PA
- Electrical Designer
We have a college campus project that need to splice new 5 KV MV-105 shielded conductor into existing 2.4KV three -conductor MV cable. The new 5KV MV cable will feed a new transformer for chiller. The existing 2.4KV three -conductor MV cable is a feeder run around 2000ft total in the tunnel all the way back to the 13.2KV -2.4KV substation in the campus. There are other 5 or 6 buildings supplied by this cable still function well.
However during the construction, the E.C. found the old existing 2.4KV three -conductor MV cable is lead sheath cable that may be installed in 1949! They have no knowledge of the lead cable such as type and size and don't know what splice kit to use.
I research online and can not find a US manufacture that produce lead sheath MV cable. I only find some manufactures in China, Saudi Arabia still produce the lead sheath cable.
Do you have any knowledge, experience, information that can share regarding the lead sheath MV cable and the splicing kit? Thank you all!