I use them all of the time with MC.



It appears you will have to either break out the screen or use an open / regular NM connector.
Or butt the sheath against the screen and just pass the individual conductors through.

Getting the right clamps is obviously the right answer, I was just curious about these things.
 
That's good to know, but I was trying to use it for 10-2 (w/gnd).

It's not listed for 10-2. From the Halex website:

Indoors. In a dry location, use to connect flexible metallic conduit, AC, MC, or NM cable to steel outlet box or other enclosure. Miscellaneous: 3/8" size fits 1/2" knockout. Suitable For: #14/2 thru 12/3 with ground NM sheathed cable, #14-2 wire steel armored cable, 3/8" steel flexible metal conduit, aluminum cont. corrugated metal clad cable 0.365-0.519" diameter aluminum smooth sheath metal clad cable 0.345-0.525" diameter aluminum interlocked metal clad cable 0.455-0575" diameter rect. aluminum cont. corrugated metal clad cable 0.277" x 0.375", steel interlocked metal clad cable 0.435-0.547" diameter.
 