It’s a 10-unit apartment building, ~40-50 years old. It’s for sale and they’ve asked me about opinions regarding the electrical setup.
Heating is by a central gas boiler unit with tubing through the slab to each unit (each one being a zone) with baseboard hydronic units. The boiler is shot. They’re worried about the integrity of the piping through the slab. Their thoughts are to abandon that type of heat and use electric base heat and a PTAC in each unit.
Right off the bat I told them service size was not adequate for that increase in load and would need to be upsized if they buy it. They said they’ll use that information to help them negotiate a better price.
I’m sure that I’ll have additional questions regarding a service upgrade for this project if it goes forward, but for now my question is related to an individual unit.
Each unit has a feeder from the MDP with a 70 amp breaker. In each unit there is an 8 space MLO panel. It feeds the electric range (40A) and (4) 20-amp circuits for lights and receptacles.
Ideally each unit would have a 100-amp panel. Then I could add some baseboard heat and a PTAC unit in each unit.
To be economical, rather than try to change out each panel/feeder/breaker/etc, I’m wondering about adding another panel in each unit just for the heat load. It would be fed from the new (added) DP in the mechanical room.
Generally that seems simpler.
I’m looking for feedback regarding this idea regarding code. Am I missing anything that I should be aware of?
Thanks.
Heating is by a central gas boiler unit with tubing through the slab to each unit (each one being a zone) with baseboard hydronic units. The boiler is shot. They’re worried about the integrity of the piping through the slab. Their thoughts are to abandon that type of heat and use electric base heat and a PTAC in each unit.
Right off the bat I told them service size was not adequate for that increase in load and would need to be upsized if they buy it. They said they’ll use that information to help them negotiate a better price.
I’m sure that I’ll have additional questions regarding a service upgrade for this project if it goes forward, but for now my question is related to an individual unit.
Each unit has a feeder from the MDP with a 70 amp breaker. In each unit there is an 8 space MLO panel. It feeds the electric range (40A) and (4) 20-amp circuits for lights and receptacles.
Ideally each unit would have a 100-amp panel. Then I could add some baseboard heat and a PTAC unit in each unit.
To be economical, rather than try to change out each panel/feeder/breaker/etc, I’m wondering about adding another panel in each unit just for the heat load. It would be fed from the new (added) DP in the mechanical room.
Generally that seems simpler.
I’m looking for feedback regarding this idea regarding code. Am I missing anything that I should be aware of?
Thanks.